ELECTRICAL WORKS IN
BUILDINGS - METHODOLOGY
A. METHOD
OF CONDUITING, BOX FIXING & INTERNAL WIRING
1. Carry out
the work as per the latest approved drawings confirmed by the concerned Project
Engineer. All electrical conductors shall be of sufficient size and current
rating for the purposes for which they are to be used.
2. Use
medium /heavy gauge rigid PVC Conduit: 20 /25 /32 mm diameter, 2mm thick black
colour and of ISI approved make, as indicated in drawing.
3. Conduits
should be laid between the reinforcement of slab and properly fastened to the
reinforcement with binding wires.
4. Care
should be taken to see that the conduits are held in position and the cement
grout does not enter the conduits while concreting and no conduits get damaged
due to movement of laborers on the slab before pouring and during pouring for
inspection of conduits & joints. For the floor conduiting care should be
taken that conduiting is done only just before the flooring works starts.
5. Vertical
conduits in wall chase to be properly fixed in position at the location
indicated in the drawing. Horizontal runs of conduits in wall to be avoided as
far as possible. In hollow blocks, horizontal chases are not permitted.
6. Bends in
conduit pipes should not be sharp. In embedded conduiting bends made with
bending spring with large radius should be used. The maximum bending radius
allowed in any conduit is 2.5 times the diameter of the conduit. The use
of readymade bends should be avoided as far as possible.
7. Switch
boxes to be recessed in the wall in such a way that it should be projecting 1-3
mm from wall plaster. The thickness of plaster shall be ascertained with button
or bull marks and confirmed by site engineer. The boxes may project a maximum
of 1-3 mm. Further, the wall finish such as lime rendering or punning, Glazed
Tiles / Marble / Granite, etc. are to be confirmed with concerned Project
Engineer. The finish will determine the projection. The idea is to ensure the
box projects 0.5mm beyond the painted surface and the edges do not break while
the wire is drawn.
8. Cover all
the boxes with thermocol and masking tape / dummy plates to avoid damages
during plastering. These covers should be removed only at the time of wiring.
9. Pass GI
pull wires of 16-gauge inside the conduits with additional loop length of 15cm
as draw wire.
10. The wiring
cables to be of ISI approved make, PVC insulated, stranded copper and 1100V
grade. Use following cross section for wiring.
6
Sqmm - Sub
mains (or as per drawing)
4
Sqmm - Power Circuit
2.5
Sqmm - Lighting Circuit
Earthing for Sub mains
1.5
Sqmm - Light point wiring, 5A socket outlets & fan
circuits
Earthing for Power Circuits
1
Sqmm - Earthing
for light point wiring, 5A socket outlets & Fan Circuits.
11. Red,
Yellow, and Blue for phases, Black for Neutral and Green for earth – colour
coding for wires must be followed.
12. Expansion
coupler shall be used when conduit passes through building expansion joint. One
end of the expansion coupler shall not be glued.
13. Earthing
At every light point earthing terminal should be provided
and connected to the earth continuity conductor. The resistance of any point of
the earth continuity system to the main earth electrode should not be more than
0.5 ohm.
Every electrical circuit and sub-circuit shall be protected
against excess current by circuit breakers. No circuit breaker other than a
linked circuit breaker shall be inserted in a conductor connected with earth.
Where metal works other than current carrying conductors is
liable to become charged with electricity, the metal works shall be earthed in
such a manner as to ensure immediate electrical discharge without danger. The
neutral conductor shall be insulated throughout and at no point it should be
connected to the earthing system.
All earth connections shall be visible for inspection and
shall be carefully made; if they are poorly made or inadequate for the purpose
for which they are intended, loss of life and property or serious personal
injury may result.
Joints in the earthing should be invariably done by means of
welding except in such locations where intermittent disconnection of joints is
necessitated for testing purpose or for the earthing connection to the body of
the equipment etc.
Use fully insulated tools while handling electric wires and
equipment.
14. Mounting
Height of Electrical Accessories
Light switch - 1250 mm above Finished Floor Level
(F.F.L.)
Bell Push - 1250 mm above Finished Floor Level
(F.F.L.)
Socket Outlet - 300 mm above Finished Floor Level
(F.F.L.)
TV/Telephone Outlets - 300 mm above Finished Floor Level
(F.F.L.)
Bedside Accessories - 600 mm above Finished Floor Level
(F.F.L.)
Socket Outlets in the Kitchen- 1140 mm above Finished Floor Level (F.F.L.) and (+300mm from
Counter Top)
Cooker Control unit 1140
mm above Finished Floor Level (F.F.L.) and (+300mm from Counter Top)
Wall Lights - 2200 mm above Finished Floor Level
(F.F.L.)
15 A in Utility for Washing Machine 900 mm above Finished Floor Level (F.F.L.)
Connection Unit for Exhaust Fan 2300 mm above Finished Floor Level (F.F.L.)
EXTERNAL CABLE LAYING
Cable laying involves two steps
Ø Trenching.
Ø Cable Pulling / Laying.
TRENCHING
Trenches are dug as per requirement of cable sizes and other
atmospheric conditions before digging route has to be finalized. The areas to
be avoided for cable laying are near sewage line, Ground-containing ashes,
Slag, Clinker, Fertilized Solid & Electrolytic Corrosion, which will affect
the life of cables.
Standard Depth of Trenches:
Ø Up to 1.1 KV = 450 to 750mm.
Ø Up to 11KV =750 to
900mm.
CABLE LAYING
Before laying the direction in which the cable is to be
pulled should first be decided. If it is a new cable no special precautions are
necessary, but if it is laying parallel to the existing cable, the core
sequence to be synchronized. Pulling force for Copper & Aluminium cables
with steel tape armour when pulled is as follows:
Ø Copper - 7 Kg
/Sqmm of total conductor area
Ø Aluminium - 2 Kg /sqmm of total conductor area
Also bending radius should be taken in to consideration.
Rating |
Single-Core Unarmoured |
Multi-Core armoured |
Up to 11KV |
15 D |
12 D |
Up to 22KV |
20 D |
15 D |
Up to 33KV |
25 D |
20 D |
D - Overall diameter of the cable
Where the cables have to be laid below ground level a trench
shall be made and a layer of sand be provided at the bottom for the cable to
lie on. One more layer is provided after laying the cable and a cable marking
tape should be provided over it before doing the back filling.
A minimum horizontal clearance of 150mm should be provided
between the cables whenever number of cables is more than one. Where cables
pass through holes or metal works precaution shall be taken to prevent
abrasions of the cables on any sharp edges.
High Voltage HV/ Extra High Voltage EHV DISTANCE
CLEARANCE:
It is desirable that Extra High Voltage (EHV) lines do not
pass above or adjacent to any building or part of building. If this cannot be
avoided, it shall have on the basis of maximum sag, vertical clearance of not
less than
For HV line up to and including 33 KV - 3.7m
For EHV lines - 3.7+0.3m for every additional 33
KV
The horizontal clearances between the nearest conductor and
any part of such building shall on the basis of maximum deflection due to wind
pressure be not less than …
For HV lines up to and including 11 KV - 1.2m
For HV lines above 11 KV and up to 33 KV - 2.0m
For EHV lines -
2.0 + 0.3m for every additional 33 KV or
TEMPORARY INSTALLATIONS ON BUILDING SITES
For temporary electricity supplies, voltage operated Earth
Leakage Circuit Breaker shall be installed. Only double insulated cables and
industrial type weatherproof socket outlets should be used for the distribution
of temporary power.
TOOLS TO BE USED BY TRADESMEN
Required tools must be available at site to ensure correct
work. Basic tools of the electrical personnel:
I |
Hand Tools |
|
|
|
|
1 |
Screw Drivers - Flat |
Small, Medium & Heavy Duty |
2 |
Screw Drivers - Star |
Small, Medium & Heavy Duty |
3 |
Cutting Pliers |
Small, Medium & Heavy Duty |
4 |
Nose Pliers |
|
5 |
Wire Stripper |
|
6 |
Line Tester |
|
7 |
Hammer |
Small, Medium & Heavy Duty |
8 |
Chisel |
|
9 |
File |
Rough, Smooth |
10 |
Hacksaw Frame |
|
11 |
Hacksaw Blade |
Ordinary, High Speed |
12 |
Ring Spanner Set |
|
13 |
Box Spanner set |
|
14 |
Metal Tool Box |
|
15 |
Crimping Tools |
Small, Medium & Heavy Duty |
16 |
Telephone Crimping tool |
|
17 |
Hole saw Cutter |
|
18 |
Bending Spring |
20 mm & 25 mm |
19 |
Curtain Spring |
|
20 |
Line Dori |
|
21 |
Blow Lamp |
|
|
|
|
II |
Power Tools |
|
|
|
|
1 |
Hammer Drilling Machine |
|
2 |
Air Blowing Machine |
|
3 |
Angle Grinding Machine |
|
4 |
Mini Drilling Machine |
|
5 |
Hammer Drill Bits |
Different Sizes |
6 |
DC Segmented/Non-Segmented Blades |
|
|
|
|
III |
Measuring Instruments |
|
|
|
|
1 |
Multimeter |
|
2 |
Digital Clamp Meter (Tong Tester) |
|
3 |
Megger |
|
4 |
Earth Resistance Tester |
|
5 |
Lux Meter |
|
6 |
Measuring Tapes |
Different Lengths |
7 |
Spirit Level |
Different Lengths |
INSPECTION METHODOLOGY FOR QUALITY ASSURANCE
Ensure:
1. All
junction boxes, fan boxes, and drop points pertain to drawing location
2. Check
Inner diameter, wall thickness and allowable tolerance for conduits has to be
done by means of Slide Caliper.
3. Binding
of all conduits to steel done properly before slab concreting
4. Solvent
cement for all joints applied properly
5. All
openings/ open ends are sealed
6. Conduits
running parallelly are not touching each other i.e. there are no voids in the
concrete
7. Test lamp
method – ensure that all electrical points are charged
8. Check of
ELCB (Earth Leakage Circuit Breaker)/ Residual Current Circuit Breaker by
random trip of electrical circuit
9. Check
with multimeter -
v Phase to neutral – 230V
v Neutral to earth – less than 2V
v Phase to Earth – 230V
10. In
contractual projects where lighting fixtures are part of the scope of work,
check the illumination levels with a Lux meter to conform to client
specifications
11. Electrical
switch plates should be flush with finished wall level
TOOLS TO BE USED FOR QUALITY INSPECTION
1. Multimeter
2. Lux meter
3. Test
lamps
4. Vernier
Calipers
5. Spirit
levels 1-2m
6. Measuring
tape