CONCRETE COVER AND
COVER BLOCKS
NOMINAL COVER (or Clear Cover)
Nominal cover is the design depth of concrete cover to all steel
reinforcements, ,including links. It is the dimension used in design and
indicated in the drawings. It shall be not less than the diameter of the
bar.
Nominal Cover to Meet Durability Requirement
Minimum values
for the nominal cover of normal weight aggregate concrete which should be
provided to all reinforcement, including links depending.on
the condition of exposure described below:
Exposure |
Nominal Cover in mm ( not less than) |
Mild |
20 |
Moderate |
30 |
Severe |
45 |
Very Severe |
50 |
Extreme |
75 |
NOTES
1. For main reinforcement up to 12 mm diameter bar for mild
exposure the nominal cover may be
reduced by 5 mm.
2. Unless specified otherwise, actual concrete cover should
not deviate from the required nominal cover by +I0 mm
3. For exposure condition ‘severe’ and ‘very severe’,
reduction of 5 mm may be made, where concrete grade is M35 and above.
* However, for a longitudinal reinforcing bar in
a column nominal cover shall in any case not be less than 40 mm, or less
than the diameter of such bar. In the case of columns of
minimum dimension of 200 mm or under, whose reinforcing bars do not
exceed 12 mm, a nominal cover of 25 mm may be used.
* For footings minimum cover shall be 50 mm.
For Minimum values of nominal cover of
normal-weight aggregate concrete to be provided to all
reinforcement including links to meet specified period of
fire resistance, refer in code section - 26.4.3
--------------------------------
There is no maximum cover, but the combination of
inherent shrinkage and other factors may make excessive cover break away from
underlying concrete
Minimum Concrete Cover for Reinforcement
Below are the specifications for reinforcement cover for
different structural members in different conditions.
a) At each end of reinforcing bar, concrete cover not less
that 25 mm or less than twice the diameter of the bar should be provided.
b) For a longitudinal reinforcing bar in a column,
concrete cover not less than 40 mm not less than the diameter of such bar
should be provided. In case of columns of minimum dimension of 20 cm or under,
whose reinforcing bars do no not exceed 12 mm, concrete cover of 25 mm to be
used for reinforcement.
c) For longitudinal reinforcing bars in a beam, not less
than 30 mm or less than the diameter of the bar.
d) For tensile, compressive shear or other
reinforcements in a slab or wall not less than 15 mm, not less that the
diameter of such bar.
e) For any other reinforcement not less than 15 mm, concrete
cover not less than the diameter of such bar.
f) For footings and other principal structural members
in which the concrete is deposited directly against the ground, cover to the
bottom reinforcement shall be 75 mm. If concrete is poured on a layer of lean
concrete, the bottom cover maybe reduced to 50 mm.
g) For concrete surfaces exposed to the weather or the
ground after removal of forms, such as retaining walls, grade beams, footing
sides and top etc. cover should not be less than 50 mm.
h) Increased cover thickness shall be provided as
indicated on the drawings, for surfaces exposed to the action of harmful
chemicals (or exposed to earth contaminated by such chemicals), acid, alkali,
saline atmosphere, sulphur, smoke etc.
i) For liquid retaining structures, the minimum cover
to all steel shall be 40mm or the diameter of the main bar, whichever is
greater. In the presence of sea water and oils and waters of a corrosive
character the covers, shall be increased by 10 mm.
j) Protection to reinforcement in case of concrete
exposed to harmful surroundings may also be given by providing a dense
impermeable concrete with approved protective coatings. In such a case the
extra cover mentioned in (b) & (i) above may be reduced.
k) The correct cover shall be maintained by cement
mortar cubes (blocks) or other approved means. Reinforcements for footings,
grade beams and slabs on a sub-grade shall be supported on precast concrete
blocks as approved by EIC. The use of pebbles or stones shall not be
permitted.
l) The minimum clear distance between reinforcing bars shall
be in accordance with IS:456 – 2000 or as shown in drawing.
Minimum Clear Cover for Reinforcement
Footings |
50 mm |
Raft Foundation - Top |
50 mm |
Raft Foundation – Bottom / Sides |
75 mm |
Strap Beam |
50 mm |
Grade Beam |
20 mm |
Column |
40 mm |
Shear walls |
25 mm |
Beams |
25 mm |
Slabs |
15 mm |
Flat Slab |
20 mm |
Staircase |
15 mm |
Retaining wall – on earth |
20 / 25 mm |
Water Retaining structures |
20 / 30 mm |
Effective cover
Effective cover = nominal cover + half dia of reinforcement
Cover block
is a precast concrete block to provide the necessary cover or spacing for the
reinforcement
bars from the formwork. PVC or Plastic Cover blocks are also available.
By placing
Cover blocks, rebar gets proper bonding with concrete and saved from corrosion.
The distance between the two cover blocks depends upon the
diameter of the rebar, the type of RCC structure, and rebar directions
(longitudinal or transverse). When the rebar diameter increases there will be
less sagging and hence the number of cover blocks requirement becomes less as
the bar dia. increases.
Average distance between Cover blocks
Slabs -
For 8mm - 60 cm and for 10mm - 70 cm. For 100 Sqm, approx. 280 nos. required
for 8 mm bars and approx. 210 nos. required for 10 mm bars.
Columns - all sides, for 12mm - 20mm - 60 -90 Cm
and above 20mm - 100 cm spacing required.
Beams - 12mm - 20 mm - 40 -70 Cm and above 20 mm
- 80 Cm required.
Footings - 60 - 70 Cm required
Various types of Cover blocks
Single Cover spacers, Multiple Cover Spacers
and Circular Spacers are in precast concrete blocks.
Clip Spacers, wheel spacers and chair spacers are PVC
material blocks.