PLUMBING WORKS IN
BUILDINGS - METHODLOGY
A. INTERNAL WORKS - Water Lines
1. Internal
pipe work in Toilets and Kitchen to be concealed and carried out as per working
drawings.
2. As per
the heights mentioned in plumbing drawings, mark the line on walls by chalk in
proper alignment and plumb
3. Start
chasing of line using a chasing machine or chisel and hammer. The chasing
should be done keeping the following points in mind.
Ø Depth - Should not be more than pipe size
Ø Width - Sufficient to
accommodate the pipe line
Ø Alignment - Straightness should be considered
Ø Height - For all
fittings height as given in Drawing
5. Check
Class / Specifications of Materials.
Ø High Pressure threaded Blue UPVC
Pipes of Schedule 80 to be used for cold water pipes made of ASTM IS-1785 and
threaded as per IS 1239 (Part I)
Ø Class 1 Copper pipes as per BS 2871
Part 1 and fittings as BS 864 Part II should be used for Hot Water.
Ø G.I Fittings should be used for cold
water – pipe work as per IS 1239 (Part II)
6. Prepare
pipe-skeleton and check all joints for proper tightness. Only approved make
pipes, pipe fittings and accessories including jointing materials should be
used
7. Groove
chasing should not exceed 30 mm after rough plaster for cold water supply line
and cold feed line and 50 mm for hot water supply lines.
8. While
threading UPVC pipe at site, ensure square cut of pipe ends, chamfer the ends
with a file, insert proper size wooden plug in the pipe end and then carryout
threading. The sharp edges of gripping vice and other handling tools should be
muffed with a suitable packing to prevent damage of pipe surface.
9. The
joints should be made with hand tightening of the fitting over pipe and covered
with proper layer of Teflon tape. To make the joint permanent, one to two turns
over the hand tightened joint is sufficient. Avoid over tightening as this may
damage both the pipe and fittings.
10. Special
care should be taken while connecting UPVC pipe with G.I Fittings. High quality
shellac should be used for jointing.
11. Water
tightness of line to be checked using pressure testing equipment. All other
openings should be plugged except end portions to which pressure gauge machine
is connected.
12. The
pressure reading should be above 7 kg/cm2 (80 PSI); and there should not be
even a single drop of water coming out of the joints during testing. The
duration of the test is 24 hours.
13. Apply
bitumen paint over the G.I pipe work.
14. All the
bore pieces projecting out should be minimum 200 mm from plastered surface.
15. Cover the
skeleton including fittings with good quality Hessian cloth and tie it properly
for cold water pipe work.
16. Fix the
skeleton in wall using 40 mm plumbing nails at a distance of 230 mm on
alternate side.
17. Do the
pressure testing once more after fixing in position and ensure no leakage.
18. Keep a gap
of 10 mm between all pipes and fittings to accommodate thermal expansion and
contraction of pipes for longer life of the system.
19. Horizontal
lines within bathrooms should be cement encased and tested before compacting of
sunken floor to avoid any accidental damages.
20. Curing
should be done over the plaster for at least 7 days.
Installation Guide For Copper Pipes (Hot Water Lines)
1. Make sure
that you have the correct size fittings and tube.
2. Prepare
the end of the tube by cutting to the correct length with a tube cutter or fine
bladed hacksaw. The ends of the tube must be cut square to the axis and be
especially careful not to damage the ends of the tube. After cutting the tube,
you will notice some rough edges around the outside and inside of the tube.
This is called burr and should be removed with a file or sharp blade.
3. Clean the
outside surface of the tube that will eventually go into the socket of the
fitting, along with the inside surface of the fitting.
4. Apply
water soluble flux to the tube and fitting by smearing a thin film of FLOWFLEX
Flux around the outer ends of the tube that have been cleaned and to the inside
of the cleaned socket of the fitting. This is best done with a small brush to
avoid applying too much and to prevent contact with the skin.
5. Insert
the tube into the fitting and push home until the stop is reached and wipe off
any excess flux with a clean cloth.
v For Integral Solder Ring Fittings
(Inbuilt):
6. Apply heat
to the assemble joints to be made using a conventional blow Lamp torch or
similar appliance that emits flame that is clean, blue and soot-free. Once a
complete ring of solder has appeared around the mouth of the fitting, turn off
the heat. The complete silver coloured ring of solder is proof of a sound
joint.
v For End feed Fittings:
7. Apply the
flame to the fitting to heat tube and solder cup of fitting until solder melts
when placed at the joint of tube and fitting. Allow the joint to cool without
disturbance.
8. Remove
the flame and feed solder into the joint at one or two points until a ring of
solder appears at the end of the fitting. The correct amount of solder is
approximately equal to 1 ½ the diameter of the fitting ¾” long solder for 15mm
fitting etc.
9. Wipe off
any excess flux and residues, with wiping cloth after the joints cooled
B. INTERNAL WORKS - UPVC TRAPS
INSTALLATION:
1. Determine
correct location of ‘P’/ ’Q’/ ‘S’ Traps and set it on a firm base located
relative to the floor finish by pouring concrete on a slab.
2. Bedding
can be carried out by pouring concrete around ‘P’/ ’Q’/ ‘S’ Trap; ensuring that
outlet of Trap is left clear on concrete.
3. Apply
rubber lubricant on W.C. connector ring as well as on outer side of WC
pan
4. The
outlet can be inserted in the socket end of pipe / fittings (as the case may
be) and joint can be solvent cemented to make a leak proof joint.
JOINTING INSTRUCTIONS
1. Make sure
the spigot end and inside of the socket is clean and the sealing ring is placed
evenly in the socket.
2. When
cutting pipes, make sure they are cut square. Chamfer the end cut to an angle
of 15 0 with a medium file. Cutting of pipes should be straight, as diagonal
cutting leads to leakages
3. A correct
depth of entry of the spigot into the socket is required to allow thermal
movement. To achieve this, push spigot fully into the socket (remove sealing
ring at this time) and make a mark on the spigot. Withdraw the spigot by 10 mm
& mark the spigot with the bold line. This bold mark indicates the correct
depth of entry to allow the necessary expansion gap.
4. Smear
rubber lubricant evenly on the chamfered spigot and the sealing ring. Then
insert the spigot into socket with light twisting motion. Pull out the pipe to
allow 10 mm expansion gap.
5. Maximum
Support Distance In Meter:
Size in mm |
40 |
50 |
75 |
110 |
160 |
Horizontal |
0.4 |
0.5 |
0.75 |
1.1 |
1.6 |
Vertical |
1.2 |
1.5 |
2.00 |
2.00 |
2.00 |
C. EXTERNAL PIPE WORK
1. Spacing
of inspection chambers and manholes should be such that cleaning of sewer lines
can be done easily.
2. Inlets
and outlets of chambers and manholes are to be plugged during progress of the
work. It should remain plugged till completion of the sewer lines up to
disposal so as to avoid blockage / choke-up of sewer pipeline.
3. Ensure
gully’s/channels of inspection chambers/manholes have given a smooth curve if
sewer lines are intersecting at right angles.
4. Bottom of
gully’s/channels should be laid in slope at inlet to outlet of chambers and
should be finished smooth.
5. All sewer
pipes, traps and other fittings should be free from cracks, holes and burrs
etc., and to be checked before being put into use.
6. Outflow
of chamber should have 25 mm (1”) drop than in flow of chamber.
7. Joints of
sewer pipes to be plugged with cotton yarn (packing rassi) before applying
cement slurry over joints.
8. Heavy-duty
chamber covers are to be used in parking and on road whereas light duty covers
may be used for other places. The covers used in manholes in sewer lines shall
invariably bear the word, ‘SEWER’ on the top and those used for storm water
drains shall bear the word ‘STORM’.
D. SOIL WASTE & RAIN WATER (S.W.R) DRAINAGE SYSTEM
JOINING INSTRUCTIONS:
1. Use only
rubber lubricant for joining SWR pipes & fittings, where rubber ring is
used.
2. Avoid
misalignment of vertical SWR pipe stacks and incorrect spacing of pipe clips.
3. All entry
to main stacks should be protected with water seal trap, wherever there is
mixing of soil & waste lines.
4. Keep a
gap of 10 mm between all UV stabilized SWR pipes and fittings to accommodate
thermal expansion and contraction of pipes for longer life of the system.
5. Smoke
test should be avoided and test plug / socket plug should be used for testing
the lines.
6. Horizontal
lines within bathrooms should be cement encased and tested before compacting of
sunken floors to avoid any accidental damages.
7. When
cutting pipes make sure they are cut square. Chamfer the end cut to an angle of
150 with a medium file.
8. A correct
depth of entry of the spigot into the socket is required to allow the thermal
movement. To achieve this, push spigot fully into the socket (remove sealing
ring at this time) and make a mark on the spigot. Withdraw the spigot by 10 mm
& mark the spigot with a bold line. This bold mark indicates the correct
depth of entry to allow the necessary expansion gap.
9. Smear
rubber lubricant evenly on the chamfered spigot and the sealing ring. Then
insert the spigot into socket with light twisting motion. Pull out the pipe to
allow 10 mm expansion gap.
10. Tubes
installed underground, laid on floors or in other inaccessible places must be
able to withstand twice the maximum working pressure.
11. While
laying big pipelines provision should be made for expansion joints, air vents
and proper anchorage. In case of longer runs provide air valves at all higher
points of ground and the size of the valves should be ¼th of the main line.
12. For large
diameter and higher class pipes (6 kg / cm2 and above) always use heavy-duty
solvent cement. Within 24 hours, the rigid PVC pipes are ready for use.
TESTING NON-PRESSURE INSTALLATION ABOVE
GROUND
The SWR drainage system can be put to use immediately after
installation, as no waiting time is required for joints to be set and dried.
However for testing, seal hermetically all openings below the top of the
section to be tested. The water level shall then be raised to a height of not
less than 3 meter above the highest point of the section being tested. Every
joint shall be carefully examined for leaks
E. DUCT & HIGH LEVEL PIPEWORK
1. Pipe work
in ducts and voids shall be supported from specially designed mild steel
brackets and cantilevers with swinging hangers. Roller type supports and ‘U’
bolt clips shall be used.
2. The
brackets shall be provided and fixed to the sidewalls, beams and ceilings,
where a bracket or support carries more than one pipe of different sizes, the
spacing of the brackets or supports shall be that specified for the smallest
size of pipe.
3. All pipes
must be kept at least 150 mm from lighting and power cables or conduits.
4. Pipes
shall be spaced in ducts and below floors in a manner, which will permit
subsequent access to any pipe for maintenance or removal without disturbance to
the remaining pipes.
5. All
piping shall be grouped wherever practical and shall be erected to present a
neat appearance. Pipes shall be parallel to each other and fixed at right
angles to structural members and shall give maximum possible headroom. All pipe
drops shall be truly vertical.
6. All pipes
must be supported in such a manner so as to allow free movement for expansion
and contraction and graded to the required levels for air elimination and
drainage.
F. RETICULATED LPG SYSTEM
1. The Gas
Cylinder bank provided, is equipped with a manifold to which the cylinders are
connected. Each point of connection of the cylinder to the manifold has got a
Non Return Valve to take care of any emergency arising out of failure of the
Cylinder Pigtail.
2. To take
care of excess Pressure build up in the pipeline after the regulator, an Over
Pressure Shut Off system coupled with the Regulator is provided.
3. As far as
the pipeline is concerned, there will be no threaded joints in the pipeline.
The pipeline would be necessarily DC Socket welded and hydro tested in line
with the code requirement.
4. Moreover,
leak detectors may also be installed in the Gas Cylinder bank, which would give
an audiovisual indication once the LPG level in the enclosure increases beyond
safe limits.
TOOLS TO BE USED BY TRADESMEN
Required tools must be available at site to ensure correct
work. Basic tools of the plumbing gang are:
1. Chisel
2. Pipe
Wrench
3. Chain
Wrench
4. Sledge
Hammer
5. Screw
Driver
6. Bench
Vice
7. Pipe Vice
8. Die Set
9. Hammer
Drilling M/C
10. Mini Angle
Grinding M/C
11. Drill
12. Chasing
Machine
13. Spirit
Level
14. Hammer
Drill Bit
15. Grinding
Wheel
16. File
17. Measuring
Tape
18. Pressure
Testing Machine
INSPECTION METHODOLOGY FOR QUALITY ASSURANCE
1. Check the
direction of flow vis-à-vis the installation of pipes
2. The water
has to flow into the sleeve. Check for leakage and subsequently establish
whether due to faculty sealing [Insufficient application of adhesive]
3. Check for
slopes installed using spirit levels
4. Ensure
all joints are waterproofed to ensure leak proof pipes
TOOLS TO BE USED FOR QUALITY INSPECTION
1. Spirit
levels
2. Plumb bob
3. Measuring
tape
4. Related
“Good for Construction” service drawings