PRACTICAL GUIDE TO
CONCRETE MIX DESIGN
Different ingredients of concrete need to be mixed in
appropriate proportions during the production of concrete. This can be done
either by volume or by weight, the latter being more precise and scientific. It
is essential that concrete mixes be “designed” for a particular set of given
ingredients to produce specific properties of concrete in the most economical
ways.
Rational proportioning of the ingredients of concrete,
generally referred as “mix proportioning” or “mix designing” is a process by
which one can arrive at the right combination of cement, aggregates, water and
admixtures (if any) for producing concrete to satisfy given specifications. The
purpose of mix proportioning is to obtain a product that will perform to
certain predetermined requirements.
The objective of mix design is to ensure that the concrete:
1. Complies
with the compressive strength as laid down in the specifications
2. Conforms
to the specified durability requirements to resist the environment in which the
structure will be serviceable during its design life
3. has
adequate workability
4. is
capable of being mixed, transported, laid down and compacted as efficiently as
possible
5. And last
but not least, be as economical as possible.
To achieve an optimum mix proportion to fulfill the above
parameters is a challenging task. The work of mix designing is a trial and
error exercise, which need to be carried out by an experienced person in a
laboratory.
The concrete mix needs to be designed to produce the grade
of concrete having characteristic strength not less than the appropriate values
as per IS 456:2000 Table 2 . The mix also needs to be designed for adequate
workability so that it could be being mixed, transported, laid down and
compacted as efficiently as possible. Depending upon the placing conditions,
European Standard (DIN EN206) has recommended different range of workability
and these are given in Table below. In addition, the concrete has to satisfy
the durability requirements. Minimum cement content, maximum water cement ratio
and minimum grade of concrete should be as specified by IS 456. It may be noted
that the code has specified the minimum grade of concrete to be not less than
M20 for reinforced concrete constructions.
Slump suitable for different placing conditions :
(Ref: DIN EN 206)
USE OF CONCRETE |
SLUMP CLASS |
SLUMP RANGE in mm |
Kerb laying |
S1 |
10 to 40 |
Floor and hand placed pavements |
S2 |
50 to 90 |
Mass concrete foundations, Normal reinforced concrete in slabs, beams and columns and Pumped concrete |
S3 |
100 to 150 |
Trench filling, In situ piling |
S4 |
160 to 210 |
Self compacting concrete |
S5 |
>220 |
Guidelines for concrete mix proportioning
1. Data
for Mix Proportioning
The following data are required for mix proportioning of a particular grade of
concrete:
a. Grade designation
b. Type of cement
c. Maximum nominal size of
aggregate
d. Minimum cement content
e. Maximum water cement ratio
f. Workability
g. Exposure conditions as per
Tables 4 and 5 of IS456
h. Maximum temperature of
concrete at the time of placing
i. Method of transporting and
placing
j. Early age strength
requirements, if required
k. Type of aggregates,
l. Maximum cement content and
m. Whether an admixture shall or
shall not be used and the type of admixture and the condition of use.
2. Target
Strength for Mix proportioning
In order that not more than the specified proportion pf test
results are likely to fall below the characteristics strength, the concrete mix
has to be proportioned for somewhat higher target average compressive strength
fck. The margin over characteristic strength is given by the following
relation:
f’ck = fck + 1.65 * S
where
f’ck =
target mean compressive strength at 28 days.
fck = characteristics compressive
strength at 28 days, and S = Standard
deviation
Standard Deviation
The standard deviation for each grade of concrete shall be
calculated separately.
Standard deviation based on test strength of sample
1. Number of
test results of samples: The total number of test strength of samples required
to constitute an acceptable record for calculation of standard deviation shall
be not less than 30. Attempts should be made to obtain the 30 samples (taken
from site), as early as possible, when a mix is used for the first time.
2. In case
of significant changes in concrete: When significant changes are made in the
production of concrete batches (for example changes in the materials used, mix
proportioning, equipment or technical control), the standard deviation value
shall be separately calculated for such batches of concrete.
3. Standard
deviation to be brought up to date: The calculation of the standard deviation
shall be brought up to date after every change of mix proportioning.
Assumed Standard deviation
Where sufficient test results for a particular grade of
concrete are not available, the value of standard deviation given in table 26
may be assumed for the proportioning of mix in the first instance. As soon as
the results of samples are available, actual calculated standard deviation
shall be used and the mix proportioned properly.
However, when adequate past records for a similar grade
exist and justify to the designer a value of standard deviation different from
that shown in table 26, it shall be permissible to use that value.
Assumed Standard Deviation
(Ref: Table 1 of IS 10262:2007)
Grade of Concrete |
Assumed standard
deviation N/mm2 |
M10 |
3.5 |
M15 |
|
M20 |
4.0 |
M25 |
|
M30 |
5.0 |
M35 |
|
M40 |
|
M45 |
|
M50 |
|
M55 |
A. Selection of Mix Proportions
1. Selection
of water cement ratio
Since different cements, supplementary cementitious
materials and aggregates of different maximum size, grading, surface texture,
shape and other characteristics may produce concretes of different compressive
strength for the same free water cement ratio, the relationship between
strength and free water cement ratio should preferably be established for the
materials actually to be used. In the absence of such data, the preliminary
free water cement ratio (by mass) corresponding to the target strength at 28 days
may be selected from the established relationship if available. Otherwise, the
table 17 may be used as a starting point for selection of water cement ratio
for respective environment exposure conditions.
Note: The supplementary cementitious materials that is ,
mineral admixtures shall also be considered in water cement ratio calculations
in accordance with table 17.
The free water cement ratio selected should be checked
against the limiting water cement ratio for the requirements of durability and
the lower of the two values adopted
2. Selection
of Water content
The water content of concrete is influenced by a number of
factors such as, aggregate size, aggregate shape, aggregate texture,
workability, water cement ratio, cement and other supplementary cementitious
material type and content, chemical admixture and environmental conditions. An
increase in aggregates size, a reduction in water cement ratio and slump, and
use of rounded aggregates and water reducing admixtures or fly ash will reduce
the water demand. On the other hand increased temperature, cement content,
slump, water cement ratio, aggregate angularity and a decrease in the
proportion of the coarse aggregate to fine aggregate will increase water
demand.
The quantity of maximum mixing water per unit volume of
concrete may be determined from Table 27. The water content in table 27 is for
angular coarse aggregate and for 25 mm to 50 mm slump range. The water estimate
in table 27 can be reduced by approximately 10 kg for sub angular aggregates, 20kg
for gravel with some crushed particles and 25 kg for rounded gravel to produce
same workability. For the desired workability (other than 25 mm to 50 mm slump
range) the required water content may be established by trial or an increase by
about 3 percent for every additional 50 mm slump. This illustrates the need for
trial batch testing of local materials as each aggregate source is different
and can influence concrete properties differently. Water reducing admixtures or
super plasticizing admixtures usually decrease water content by 5 to 10 percent
and between 10 to 30 percent respectively at appropriate dosages.
Maximum water content per cubic metre of concrete for
nominal maximum size of aggregate
(Ref: Table 2 of IS 10262:2007)
Nominal Maximum size of aggregate, mm |
Maximum water content,
kg** |
10 |
208 |
20 |
186 |
40 |
165 |
** - Water content corresponding to saturated surface dry
aggregates.
Note: These quantities of mixing water are for use in
computing cementitious material contents for trial batches.
B. Calculation of Cementitious Material Content
The cement and supplementary cementitious material content
per unit volume of concrete may be calculated from the free water cement ratio
and the quantity of water per unit volume of concrete.
The cementitious material content so calculated shall be
checked against the minimum content for the requirements of durability and
greater of the two values adopted. The maximum cement content shall be in
accordance with IS 456.
1. Estimation
of Coarse Aggregate Proportion
Aggregates of essentially the same nominal maximum size,
type and grading will produce concrete of satisfactory workability when a given
volume of coarse aggregate on rodded density basis, is used per unit volume of
concrete. Approximate values for this aggregate volume are given in table 28.
It can be seen that for equal workability, the volume of coarse aggregate in a
unit volume of concrete is dependent only on its nominal maximum size and
grading zone of fine aggregate. Differences in the amount of mortar required
for workability with different aggregates, due to differences in particle shape
and grading, are compensated for automatically by differences in rodded void
content.
Volume of Coarse Aggregate per unit volume of concrete
for Different Zones of Fine Aggregate
(Ref: Table 3 of IS10262:2007)
Nominal maximum size of Aggregate in mm |
Volume of Coarse Aggregate** per unit volume of concrete
for different zones of
Fine Aggregate |
|||
Zone IV |
Zone III |
Zone II |
Zone I |
|
10 |
0.50 |
0.48 |
0.46 |
0.44 |
20 |
0.66 |
0.64 |
0.62 |
0.60 |
40 |
0.75 |
0.73 |
0.71 |
0.69 |
** Volumes are based on aggregates in saturated surface dry
condition
For more workable concrete mixes which is sometimes required
when placement is by pump or when the concrete must be worked around congested
reinforcing steel, it may be desirable to reduce the estimated coarse aggregate
content determined using Table 28 up to 10 percent. However, caution shall be
exercised to assure that the resulting slump, water cement ratio and strength
properties of concrete are consistent with the recommendations of IS 456 and
meet project specification requirement as applicable.
2. Estimation
of Fine Aggregate Proportion
With the completion of above procedure, all the ingredients
have been estimated except the coarse and fine aggregate content. These
quantities are determined by finding out the absolute volume of cementitious
material, water and the chemical admixture; by dividing their mass by their
respective specific gravity, multiplying by 1/1000 and subtracting the result
of their summation from unit volume. The values so obtained are divided into
coarse and Fine Aggregate fractions by volume in accordance with coarse
aggregate proportion already determined. The coarse and fine aggregate contents
are then determined by multiplying with their respective specific gravities and
multiplying by 1000.
3. Combination
of Different Coarse Aggregate Fractions
The coarse aggregate used shall conform to IS 383. Coarse
aggregates of different sizes shall be combined in suitable proportions so as
to result in an overall grading conforming to Table 2 of IS 383 for particular
nominal maximum size of aggregate.
Determination of mass per m3 yield and cement factor of
freshly mixed concrete shall be carried out as per IS 1199.
C. Trial Mixes
The calculated mix proportions shall be checked by means of
trial batches.
Workability of the trial mix no.1 shall be measured. The mix
shall be carefully observed for freedom from segregation and bleeding and its
finishing properties. If the measured workability of trial mix no.1 is
different from the stipulated value, the water and /or admixture content shall
be adjusted suitably. With this adjustment, the mix proportion shall be
recalculated keeping the free water cement ratio at the pre selected value,
which will comprise trial mix no.2. In addition two mor trial mixes no.3 and 4
shall be made with the water content same as trial mix no.2 and varying the
free water cement ratio by +/- 10 percent of the pre selected value.
Mix no.2 to 4 normally provides sufficient information,
including the relationship between compressive strength and water cement ratio,
from which the mix proportions for field trials may be arrived at. The concrete
for field trials shall be produced by methods of actual concrete production.
D. AN ILLUSTRATIVE EXAMPLE OF CONCRETE MIX PROPORTIONING
DESIGN MIX FOR M20
01. |
Grade designation |
M20 |
02. |
Type of Cement |
OPC 53 grade |
03. |
Maximum nominal size of aggregate |
20 mm |
04. |
Minimum cement content |
300 kg/m3 |
05. |
Maximum water cement ratio |
0.55 |
06. |
Workability |
130 mm (Slump) |
07. |
Exposure Condition |
Mild |
08. |
Method of concrete Placing |
Pumping |
09. |
Degree of Supervision |
Good |
10. |
Type of Fine Aggregate |
Natural River Sand and Crushed Rock fines |
11. |
Type of Coarse Aggregate |
Crushed Rock |
12. |
Maximum cement content |
450 Kg/m3 |
13. |
Type of Chemical Admixture |
Super plasticizer. |
14. |
Brand of Admixture |
BASF Rheobuild 4839 |
TEST DATA FOR RAW MATERIALS
1. Cement
used OPC 53grade conforming IS12269
2. Specific
gravity of Cement 3.15
3. Specific
gravity of coarse aggregate 2.65
4. Specific
gravity of Fine aggregate 2.61
5. Water
absorption of coarse aggregate 0.5
percent
6. Water
absorption of Fine aggregate 1.0
percent
7. Sieve
analysis of Fine aggregate
IS Sieve Designation |
Cumulative Percentage passing |
Cumulative %
passing when river sand & stone dust are mixed in 70:30 |
Requirements for Zone II as per IS:383-1970 (% Passing) |
|
River Sand |
Stone Sand |
|||
4.75 mm |
98.5 |
100 |
98.95 |
90 – 100 |
2.36 mm |
93.3 |
100 |
95.31 |
75 – 100 |
1.18 mm |
66.3 |
77 |
69.51 |
55 – 90 |
600 microns |
41.0 |
56 |
45.5 |
35 – 59 |
300 microns |
14.3 |
33 |
19.91 |
8 – 30 |
150 microns |
7.4 |
6 |
6.98 |
0 – 10 |
8. Sieve analysis of Coarse aggregate
IS Sieve Designation |
Cumulative% Passing 20mm |
Cumulative% Passing12.5 mm |
Cumulative% passing when
20mm & 12.5mm are mixed in 58:42 ratio |
Requirements of Cum. %
passing for 20mm graded agg . as per IS:383-1970 |
20 mm |
98.25 |
100 |
98.98 |
95 – 100 |
16 mm |
54.25 |
100 |
73.46 |
--- |
12.5 mm |
21.75 |
95.84 |
52.86 |
--- |
10 mm |
2.75 |
61.68 |
27.50 |
25 – 55 |
4.75 mm |
---- |
0.20 |
0.08 |
0 – 10 |
Design Mix calculation for M20 grade
Target Strength for Mix Proportioning F’ck = Fck
+ 1.65 * S
Where
F’ck = target average compressive strength at 28 days. Fck =
Characteristics compressive strength at 28 days. S = Standard deviation
From IS 10262:2007, Table 1, standard deviation S = 4 N/mm2
Therefore, Target Strength = 20 + 1.65*4 = 26.66 N/mm2
Selection of Water-Cement Ratio
From IS 456:2000, Table 5, Maximum water cement ratio = 0.55
Based on experience, adopt water cement ratio as 0.53
0.53 < 0.55, hence OK.
Selection of Water Content
From IS 10262:2007, Table 2, Maximum water content for 20 mm
aggregate = 186 Kg (for 25 mm to 50mm slump range)
Estimated water content for 100 mm slump =186 + 3/100 * 186
=192 Kg
As super plasticizer is used, the water content can be
reduced up to 30 percent.
Based on trials with super plasticizer water content
reduction of 17 percent has been achieved. Hence the arrived water content =
192 * 0.83 =159.36 Kg
Calculation of Cement content
Water cement ratio = 0.53
Cement content =159/0.53 =300 Kg/m3
Check for exposure condition from IS 456, Table 5 Minimum
cement content 300 Kg/m3
Hence, OK.
Proportion of volume of coarse aggregate and Fine
aggregate content
From Table 3, Volume of coarse aggregate corresponding to 20
mm size aggregate and fine aggregate Zone II = 0.62
For Pumpable concrete these values should be reduced by 10
percent Therefore volume of coarse aggregate = 0.62*0.93 = 0.5766
Volume of fine aggregate content = 1 - 0.5766 = 0.4234
Mix Calculations
Volume of Concrete = 1 m3
Volume of cement =
(Weight. of cement/Sp.gravity of cement) * (1/1000)
= (300/3.15) * (1/1000)
= 0.0952 m3
Volume of Water =
(Weight. of water/Sp.gravity of water) * (1/1000)
= (159/1) * (1/1000)
= 0.159 m3
Volume of chemical = (Weight. of Admixture/Sp.gravity of
Admixture) * (1/1000) Admixture
= (1.8/1.19) * (1/1000)
(@0.6% by mass of =
0.0015m3 Cement)
Volume of all in =
(1-(0.0952+0.159+0.0015)) Aggregate =
0.7443 m3
Mass of Coarse =
0.7443 * 0.5766 * Sp.gravity of C.A * 1000 Aggregate
= 0.7443 * 0.5766
* 2.65 * 1000
= 1137.28 say
1130 Kg
Mass of Fine =
0.7443 * 0.4234 * Sp.gravity of F.A * 1000 Aggregate
= 0.7443 *
0.4234 * 2.61 * 1000
= 822.50 say 810 Kg
MATERIAL REQUIRED FOR M20 GRADE - ONE CUM OF CONCRETE
01. Cement
- 300 Kg
02. Free Water
- 159 Kg.
03. River Sand
- 570 Kg.
04. Crushed
Rock Fines - 240 Kg
05. Coarse
Aggregate - 20 mm - 660 Kg
12 mm - 470 Kg
06. Admixture - 1.80Kgs.
07. Water for
Absorption (CA & FA ) - 14.0 Kg
08. Total Water
- 173 Kg
Free Water Cement Ratio -
0.53
Note: Weight Batching correction for Surface Moisture
in Aggregates Should be Carried out Regularly.