RCP
TEST- WATER PERMEABILITY TEST - SALT PONDING TEST
Concrete is a composite
material comprising of Cement, Sand & coarse aggregate. Every material has
pores, which contains voids in it. Aggregates have a more substantial void
ranging from 1mm to 10mm which cement paste fills these. Even cement has voids
ranging from 1micron to 10micron. Due to this interconnected and continuous
link to fill one void by other material concrete is prone to permeate fluid or
gases into it.Or In simple words, Presence of voids in concrete makes permeable
which in turn allows water or gas to flow into it. The permeability of concrete
is the ability of concrete to resist the water flow or any other substance into
it when the external force is applied.
Durability of concrete is
most important and complex property of concrete. If concrete is permeable,
deleterious materials like water, CO2, SO2 & Cl which permeates through the
pores of the concrete and reacts with the reinforcement forms rust which
increases the volume of the reinforcement and damages the structure. Prior
understanding of the extent and rate of permeation helps to design structure
better.
Factors affecting the
Concrete Permeability:
1. Water-Cement ratio
Excessive water is added to the concrete mix to increase the workability of
concrete. This additional mixing of water, more than required increases the
porosity in concrete and degrades the durability of concrete. To resist the
entry of water into the concrete 0.4 water-cement ratio is adopted. Experiments
proved that taking a water-cement ratio of 0.4 makes concrete impermeable.
2. Improper compaction
of concrete
Improper compaction in concrete is the major problem for porosity in concrete.
Concrete should be adequately compacted using hand compaction method or machine
compaction methods. Poorly compacted concrete leads to the formation of
honeycomb which ultimately makes steel to corrode and forms surface cracks.
3. Improper Curing
Concrete should be adequately cured by considering the atmospheric weather.
Improper curing in concrete leads to the formation of cracks and in turn, it
increases the permeability of concrete
Different purposes
to check the Permeability of concrete
1. Measuring the
Permeability of concrete as a quality control parameter: To assess and study the property of the
material that we are using or going to use. Suppose we need a zero permeable
concrete for construction. After investigating we found that there is a 2% of
porosity, then we dismiss the concrete for construction as it is not as per
specifications.
2. Evaluating the
permeability of already laid concrete structure: As an engineer, we often check the
Permeability property of concrete of older monuments or existing structures.
This type of measuring requires a Non-destructive test as cutting concrete from
the structure is not possible.
Permeability test of
concrete:
This test is more important
in RCC as we know that reinforcement is prone to corrosion when it reacts with
the water, which in turn forms a layer around the reinforcement and causes an
increase in the volume of concrete which ultimately leads to surface cracking.
To resist the reinforcement to corrode, the concrete is set to permeable and
Permeability test of concrete tests the same.
Not only the water or
moisture there are other atmospheric deleterious materials which ingress with
reinforced concrete leads to corrosion of steel.
Most commonly used
tests to measure the Concrete Permeability are
1. Rapid Chloride Permeability Test
2. Water Permeability by pressure
3. Ponding with a salt solution
1.Rapid Chloride
Permeability test [RCP Test]
For Specifications and the
quality control purposes on site, the rapid chloride permeability test
[RCPT} is simple to conduct and that can be performed in a short time.
Rapid Chloride Permeability
test is covered by AASHTO T 277 or ASTM C 1202 it is the test for chloride
ions. As the name it proves that, this test is performed to check the
Concrete’s Ability to Resist Chloride Ion Penetration.
This test is an Electrical
Indication of Concrete’s Ability to Resist Chloride Ion Penetration. This test
enables to predict the service life of concrete structures. It can also be used
for durability-based quality control purposes.
In this test, the constant
voltage (V) is applied on a concrete specimen for 6 hours and the current (i)
passing through the concrete is recorded to find the coulombs.
What is coulomb?
Current is measured in
amperes. A coulomb is an ampere – second;
Which means 1 ampere passed
through the concrete specimen in 1 second is a 1 coulomb, and the charge passed
in 60 seconds would be 60 coulombs. The more permeable the concrete, the higher
the coulombs; the less porous the concrete, the lower the coulombs.
Apparatus
This test is made possible
by an equipment which is known as Rapid Chloride Permeability test equipment,
the test equipment consists of two reservoirs. One of them has 3.0% of NaCl solution
and another reservoir has 0.3M NaOH Solution, Concrete having thickness 50mm
and dia 90-100mm is used as a test specimen.
Chloride test
procedure
1. The concrete specimen having dia 100mm and thickness 50mm is
cast and saturated.
2. The concrete sample is placed in between the two reservoirs
(which is called as a single cell) having NaCl solution in one reservoir and
NaOH solution in the other.
3. These reservoirs are connected to DC supply and the voltage
of 60V is applied to the concrete specimen at both the ends for 6 hours.
4. Now measure the current passing through the concrete at
different time intervals.
5. The current passing through the concrete is determined by an
LCD which is connected to the cell.
RCPT Test Formula
Q = 900 [I0 + 2I30+2I60+2I90+2I120+……+2I330+2I360]
Q = current flowing through
one cell (coulombs)
I0 = initial current
reading in amperes immediately after voltage is applied
It = current reading
in amperes at t minutes after the voltage is applied.
For determining the accurate
concrete permeability 2-3 samples are taken from same batch of concrete mix and
measured as mentioned, the average value is taken as a final reading.
Permeameter can have 2-3 cells with separate LCD digital meter to determine 2-3
samples at a time.
The total charge
passed is determined by the above mentioned formula and used to rate the
concrete according to the below criteria.
RCPT test is not suitable
for concrete having very low permeability and takes a lot of time for results.
2.WATER PERMEABILITY
TEST FOR CONCRETE BY PRESSURE
This test is suited and
applied to the concrete having high permeability. This test is also called
as Water Penetration test of concrete. This test is carried
out using a disc of concrete and involves water flowing out through the disc at
a steady rate.
Procedure
1. The concrete having a thickness More than 20mm is placed on
Permeameter.
2. And then the Permeameter Is filled with the water.
3. To find the permeability of Concrete the water passing
through the disc is collected at the water collection unit.
4. To accelerate the process, the pressure is applied to the
water from the top.
Water Permeability by
pressure test Formula
K = QL/ tAh
K = coefficient of permeability
Q = discharge of water into collection unit
t = elapsed time in secs.
L = top length of concrete specimen
A = top area of concrete specimen
h = applied pressure head in m
3. SALT PONDING
TEST
This test measures the
resistance of concrete to chloride ion penetration. The penetration of
chlorides into concrete is very severe when compared with the other deleterious
substances. This bought attention to most of the researchers to find the
permeability of concrete based on chlorides compared to other mechanisms.
In this test, the concrete
sample is sealed on sides and the 3.0% NaCl Solution is ponded above the
surface of the concrete.
Procedure for Salt
Ponding test
1 This test requires a large sample of concrete when compared
with the other tests. 3 concrete slabs of length & breadth 300mm x 300mm
and thickness 75mm are cast and cured for 14 days and kept in the drying room
for 28 days with a 50% relative humidity environment before conducting the
test.
2 Each concrete slab is sealed on both sides and 3% of NaCl
Solution is ponded on the top surface for 90days.
3 The bottom face of the concrete slab is left exposed to the
drying environment.
The specimens are
maintained with a constant amount of chloride solution at top surface for 90
days.
After completion of 90
days, the specimen is sliced as a layers having thickness 12mm each which means
each specimen is cut into 6 segments.
Results
If the concrete is
impervious the chloride penetration in the layers is zero.
If the concrete is more permeable
then chlorides may penetrate up to the second or third layer from top.
This test is used as a
specification writing where you can choose the strength of concrete based on
the chloride penetration. Suppose, if you want an excellent impervious concrete
you may write specification as Chloride penetration up to a layer 1.