STEEL
REINFORCEMENTS - METHODOLOGY
GENERAL INSTRUCTIONS
- Start reinforcement works with proper “Good for
Construction” drawings and general specifications as issued by the
consultant.
- Make a stage-wise BBS (Bar Bending schedule) on
the computer before indenting for steel.
- IS codes such as IS 456, IS 1786, IS 2502, SP
34 should be available at site office at any given time for ready
reference.
- Earmark the reinforcement work yard and stack
yard. Care should be taken to ensure accessibility for trailers and
availability of sufficient working space.
- In case of extreme site constraints, the
cutting and bending can be done elsewhere and transported to site.
Materials
- Mild steel bar should comply with IS 432.
- Cold worked steel high strength deformed bars
should comply with IS 1786.
- Steel weighment should be done at site by the
storekeeper by taking it to the nearest weigh bridge.
- Stack steel 300 mm clear of ground on SSM
walls.
- Stack steel -Grade wise, consignment wise,
diameter wise and length wise.
- Protect stored steel from rusting, oil, grease
and distortion.
- Ensure Mill Certificate is delivered with each
load.
- Binding wire shall be 16-gauge soft annealed
iron wire or 18 gauge GI annealed wire.
- Collect the rings used for bundling rods in
bags and store them.
- Cut pieces/ scrap should be stored separately
in an enclosed area with dunnage.
- Steel is tested for its chemical and physical
properties. Chemical tests checks for the Carbon, Sulphur and Phosporous
content, while the physical tests check the ultimate tensile strength,
Elongation, Bend and Rebend test.
CUTTING, BENDING AND
PLACING REINFORCEMENT
- Cut the rods economically to reduce wastage as
per the BBS. Start laying rods only after shuttering is totally cleaned
and oiled and checked for levels etc.
- Pitted, deformed, defective, corroded, cracks;
splits on bend bars should not be used and rejected, removed from site.
- Neither the size nor length of the bars should
vary with respect to drawings.
- Tolerance for cutting of reinforcement = +75 or
–25mm
- Bending Tolerance
= +0 or –10mm
- Bar spacing
= + or – 10mm
- Take extreme care while bending steel already
cast partially in concrete so as not to damage the concrete around the
bars.
- All laps should be 50d or as specified.
- Laps are staggered and not more than 33% of
bars shall be lapped in a particular section.
- Mechanical splicing and welding of rods should
be done only after proper details and instructions are available from the
structural consultant.
- At time of concreting, reinforcement shall be
free from mud, oil, grease, mortar dropping, mill scale or other foreign
matter.
- Give spacer blocks in CM 1:2 and cured for at
least 7days immersed in water.
- Give spacers as per specifications. Generally
15mm for slab, 25mm for beam and 40mm for the footing is provided. It
depends on the maximum size of aggregate, the reinforcement size and the
element concreted.
- Proper end bearing of rods with required
development length are the main points to check.
- Chairs should be placed as last operation
before concreting to avoid distortion of top rod due to traffic.
- Check if dowels for columns, beams and slabs
are given correctly and is of required minimum length.
- For slab reinforcement, the structural
consultant should check and certify each work before concreting.
- Highlight areas of reinforcement congestion and
get the bar arrangement revised to facilitate easy flow of concrete all
around.
- Spacer bars shall maintain vertical distance
between successive layers of bars.
- Binding wire ends after tieing should be turned
inside and should not stick out to the surface.
- Work should be neat, correct as per drawing and
specification. A separate engineer with prior experience in reinforcement
works is required to supervise works.
INSPECTION METHODOLOGY
- Steel Mill Certificate is delivered with each
load
- Adherence to reinforcement detail as per
drawings in - Sunken Areas - Inverted Beams - Columns
- Cover blocks for the above.
- Check overlapping wherever possible
- Check Binding wires – whether joints are
properly bound
- Check for chairs and their disturbance due to
movement of labour
- Columns to be checked for plumb. Check for
plumb by holding the spirit level to the formwork at various points.
- Protruding reinforcement in the balcony and
other areas to be checked for parallelity using spirit levels before and
after concreting. Supports need to be checked.
- Dowels to be checked for adequate number and
strength. Wherever walkways, or staircases or balconies have connected,
dowels to be inspected by the structural consultant before concreting.